If a device with a 4-20 mA output shows a reading of 6 mA, what is the corresponding measurement based on a range of 0-63,535?

Prepare for the CWEA Electrical and Instrumentation Grade 2 Test. Strengthen your skills with interactive questions and detailed explanations. Ensure your success!

To determine the corresponding measurement for a device with a 4-20 mA output that shows a reading of 6 mA within a scale of 0-63,535, it's essential to understand the relationship between the current output and the measurement range.

The 4-20 mA current loop operates on the principle that 4 mA represents the lower limit of the scale (0 in this case) and 20 mA represents the upper limit (63,535). To find the measurement corresponding to a 6 mA output, we first need to calculate the span of the scale, which is the difference between the maximum and minimum values:

Maximum value = 63,535

Minimum value = 0

Span = 63,535 - 0 = 63,535

Next, calculate the percentage of the output signal above the minimum (4 mA):

Current output = 6 mA

Minimum signal = 4 mA

Difference = 6 mA - 4 mA = 2 mA

Now, to find the percentage of the output within the overall range:

Percentage = (Difference / (20 mA - 4 mA)) * 100

Percentage = (2 m